完善资料让更多小伙伴认识你,还能领取20积分哦, 立即完善>
Lightning Protection – Introduction
Structural lightning protection design considerations BS 6651 (Protection of structures against lightning) clearly advises strict adherence to the provision of a conventional Lightning Protection System (LPS) – to the total exclusion of any other device or system for which claims of enhanced protection are made. Principle components of a conventional structural lightning protection system, in accordance with BS 6651 are: ? Air termination network ? Down conductors ? Earth termination network ? Bonding (to prevent side flashing). Air termination network On high risk structures such as explosive factories, no part of the roof should be more than 2.5m from an air termination conductor. This is generally achieved by applying a 5m x 10m mesh to the roof. However, for most structures, a mesh of 10m x 20m is considered sufficient, giving a maximum distance from any part of the roof to the nearest conductor of 5m. |
|
相关推荐
2 个讨论
|
|
小黑屋| 手机版| Archiver| 电子发烧友 ( 湘ICP备2023018690号 )
GMT+8, 2024-11-25 04:13 , Processed in 0.550699 second(s), Total 44, Slave 34 queries .
Powered by 电子发烧友网
© 2015 bbs.elecfans.com
关注我们的微信
下载发烧友APP
电子发烧友观察
版权所有 © 湖南华秋数字科技有限公司
电子发烧友 (电路图) 湘公网安备 43011202000918 号 电信与信息服务业务经营许可证:合字B2-20210191 工商网监 湘ICP备2023018690号